Welcome to ECN!
Here is a quick and dirty response to the Load Calculation for Demand Factor Scenario of Six Electric-Only Clothes Dryers in Dwelling Unit(s):
*** NOTE: For this example, I am basing the Dryers at 6.0 KVA, 240V 1 Phase ***
6000 VA (6.0 KVA) = 25.0 Amps at 240V 1 Phase 2 Wire
6,000 VA (6.0 KVA) x 6 Dryers = 36,000 VA (36.0 KVA)
Per Table 220.54, Demand Factor for 6 Dryers = 75% (0.75)
36,000 VA x 0.75 = 27,000 VA (27.0 KVA)
27,000 VA ÷ 240V = 112.5 Amps
Demand for this part of a Load Calculation Database:
* 27.0 KVA * 112.5 Amps
If you need practice, make up a few project examples and compile Load Calcs for each one - via what is outlined in NEC Article 220, along with the example Project Calculations found in Annex D (Annex D is at the back of the NEC Codebook); then post your scenario Projects' information + Load Calcs in this Thread, for review.
Good luck.
Scott
Scott " 35 " Thompson Just Say NO To Green Eggs And Ham!
|
|
|
Entire Thread
|
calcs,,,,,,
|
romex2121
|
06/13/10 10:33 PM
|
Re: calcs,,,,,,
|
gfretwell
|
06/13/10 11:28 PM
|
Re: calcs,,,,,,
|
romex2121
|
06/13/10 11:54 PM
|
Re: calcs,,,,,,
|
sparky
|
06/14/10 01:30 AM
|
Re: calcs,,,,,,
|
Scott35
|
06/14/10 01:39 AM
|
Re: calcs,,,,,,
|
romex2121
|
06/14/10 02:29 PM
|
Re: calcs,,,,,,
|
romex2121
|
06/15/10 08:46 AM
|
Re: calcs,,,,,,
|
HotLine1
|
06/15/10 06:08 PM
|
Re: calcs,,,,,,
|
Scott35
|
06/18/10 02:21 AM
|
Re: calcs,,,,,,
|
romex2121
|
06/19/10 05:57 PM
|
|
Posts: 144
Joined: March 2008
|
|
|
|