Hi
Went there today and thought I found problem with the frig, changed main breaker, but still the lights dim.
With main breaker on ,one leg to neatral draws 116.7v and the other leg draws 125.5v When main breaker is shut off, with no load, on the street side of the main the v on both legs is 121.5v.
When I shut off circuit brekers one at a time the voltage on the high lege will gradually go back down to match the volts on the other leg. The thing that is driving me crazy is I can not isolate the problem, it seems to be on multiple circuits. Could the outside meter be defective, PC has not checked it.
I have meeting to go to I will check back.
Thanks Mike


dukes