I never said "call U/L". It is reasonable to ask for some kind of listing tho, when the NEC specifically says

Quote
This provision shall not apply to cover-mounted receptacles unless the box and cover combination are listed as providing satisfactory ground continuity between the box and the receptacle.


It is up to the installer to demonstrate that, particularly when we are just talking about 8" of wire and a screw.


Greg Fretwell