I wired a 300 foot addition(4 lights and 10 plugs, I added it onto an existing circuit which feeds the living room plugs(no lights in there)and kitchen light and dining light. The inspector says I have to count that square footage(kit,dining and addition)to calculate my branch circuit which is feeding these. When did we start calculating for single branch circuits? Have I been missing something? This house has the number of circuits required per square footage, including the addition. So why is he making me calculate individual circuits to the existing and addition? Can anyone shed some light on this? I could pull a new circuit...but that's not what I bid, so for future bidding, if he is correct on this branch circuit/SQ FT I won't get burned again.
Thanks guys,
H2o