If you wish for this installation to pass code. You cannot enter directly into the back of the panel when through the basement foundation wall.
Yes you are correct. I seen that in section 6 after I posted the question. I think I should pop up through the garage floor then LB into the mechanical room through the foundation. I haven't done alot of services....in fact mabey 3 in my career. Should I ground the neutral in the meter base or at the panel? Am I required to pull a bond wire between the meter base and panel?
Ask me an industrial installation question or programming question and I'm ggod to go. Residential services....I need brushing up on!