Leland, that is the minisplit I was talking about. They have a low voltage air handler, fed from the condenser.
Harold is talking about an air handler with 240v 15a feed. I can't imagine why you need all that if there is no heat.
The blower is going to be a fractional HP motor.
If it is 1/8 or less then you can cite 430.81(A).
Talking about Harold's air handler, I still bet this air handler has a heat bay if it really has a 3.6kva (240a @ 15a)circuit requirement. That machine does need a disconnect within sight IMHO.


Greg Fretwell