I received a call from a customer looking to purchase an electrolux free standing range. the specs say 17kw@240 V.
I calculate this out to 70 amps.
His existing range supply is 40 amp.
The electrical specs say min 50 amp circuit.
would this range come with a cord attached already. model is electrolux CEW30EF6G.

I assume the existing wire #8 would not be suitable.

the other model is 15kw that he is looking at.
looking at the code it looks like we could only put a 14 kw on the existing range branch circuit