I don't think I would leave it that way. I would fill the holes with a press-to-test indicator and a momentary-off-on rotary selector switch. The pressure switch should have a pressure and deadband or differential adjustment. The Off position breaks path to N.C. opens on P increase, switch terminals. The momentary, "Hand" position, parallels P-switch, to check operation without bleeding the tank. The N.O. aux switch would be used to drive your indicator. Do you have any E-stops in the mix? You wouldn't need any holding contacts unless you were going to use 2 separate pressure switches in series. In that case, the holding contact is in parallel with the low pressure switch. It helps to think of one as "closes on low pressure", and the other as, "opens on high pressure"
Joe