No way - these are DII (0.5-25amps). I think these two fuses are either the only two circuits for the entire place (maybe 6, 10 or 16 amps) or (looking at some of the other pictures) hot and neutral fuse for the only circuit.

So the last picture is actually the repaired version... nice!

The far left arrangement clearly took the load side conductors directly to the meter line side conductors, bypassing meter and fuses... regarding the burnt panel I'm not sure what happened - either they disconnected the service and taped the wires or they (shoddily) bypassed the meter.

At any rate the key ring (epreventing overfusing) was missing, otherwise the screwdriver trick couldn't have worked at all.

The rotary switch sure is 3 phase... look how the breakers are split over the three wires. 3 3ph breaker hidden by a floating single phase breaker is nice too...