Rule 24-104, in the "Patient Care" section, mandates the use of a insulated bonding conductor, unless insulated by way of a non conductive raceway or by the construction of the cable containg the conductor.

Rule 4-036(1) mandates that a insulated grounding or bonding conductor be green or green with a yellow stripe.

Using any other color as a bonding or grounding conductor, is permitted only if the conductor is a #2 or larger and if it is permanetly re-identified as required by 4-036(1b) and "no", tape is not adequate in my books.

Last edited by Rick Kelly; 03/29/08 11:41 AM.