I recieved some violations:

1. Provide suitable outlet boxes for all installed emergency lighting and exit sign equipment identifying it as suitable for connection to a metallic wiring method, or provide access to this equipemtn to verify internal bonding means. MEC 314.3


....what I did was ran MC, from a j-box went over a foot, then through a concrete block into the back of an all plastic emergency light., no internal bonding avalible. This is Michigan so MC cannot be used for grounding/bonding.

wait, wait ok I guess could open my code book every once in awhile.. I would need non metallic. How should I do this... put a j-box in the opposite side of the cement block and run... erm.. something non metallic... romex? that doesn't sound right... its an old apartment building they turned into condos.