Under B.C.Amendments
(www.safetyauthority.ca/files/Amendments%20to%20Electrical%20Code.pdf) 12-116 reads as follows:
(Italic are added subrules from the amendments)

12-116 Termination of conductors
(see Appendix B)
(1) Connection of conductors to terminal parts shall be made by means of pressure connectors, solder lugs or
splices to flexible leads.

(2) The portion of stranded conductors to be held by wire-binding terminals or solderless wire connectors shall
have the strands confined so that there will be no stray strands to cause short-circuits or grounds.

(3) Stranded and solid conductors No. 10 AWG and smaller shall be permitted to be connected by means of
wire-binding screws, or studs and nuts that have upturned lugs or equivalent.

(4) Stranded and solid conductors larger than No. 10 AWG shall be terminated in solderless wire connectors or
shall be permitted to be soldered into wire connectors specifically approved for the purpose except where
prohibited by Section 10.

(5) Terminals for more than one current-carrying conductor shall be specifically approved for the purpose and be
so marked.


These are B.C. Amendments I don't know about Ontario.