Service wires are only required to be sized to the computed load (230.42) not by the breaker since the service wires are up stream of the main breaker. The service wires are protected by the POCO OCPD at the transfomer. OCPD only protects wires down from the device, not up. Your local AHJ may have other restrictions. What is the computed load?