Very straight forward bathroom remodel and I failed the final inspection.

The inspector says the Panasonic exhaust fan-light needs to be GFCI protected. It is NOT above the tub, but approx 2' away from the tub centered in the remainder of the bathroom. I realize if it were above the tub it would need GFCI protection per 110.3(B). He says it is in the bathtub area which is 3' horiz. away from the tub.

I believe he is confused with 410.4(D) which does not allow (GFCI or not) a hanging light or PADDLE fan in that area. I don't want to bust holes, fish wires or pay $45 for a GFCI breaker.

Am I missing something??