here is some more
the max tension should not exceed .008 times of the CM when pulled with a pulling eye attached to the copper conductor

Tm =.008 x N x CM

Tm = max pulling tension,9lbs)

N = number of conductors being pulled

CM = circular mill area of each conductor

there is a bit more to this than I typed..now I'm curious, are you having problems pulling that wire out ??

Last edited by togol; 06/25/07 01:33 PM. Reason: punctuation

Tom