And at 120 Volts 360.8 amperes LINE to NEUTRAL.

You guys are using line to line; not line to neutral.

The vast bulk of the loads in the panel will be at 120V. These are line to neutral loads.

When you inspect a dry type transformer you will note that the high side is delta connected -- line to line -- 480 volts. The load side windings are connected wye with a turns ratio of 4:1.

The line to line of 208A at 208V would be used if you had a delta/wye transformer running 208 delta to 208/120 wye. They are made typically as isolation transformers when the Service is 208/120 wye but isolation is desired. Such a transformer would still produce 360.8 line to neutral amps if it was 75kVA.

Last edited by Tesla; 05/24/07 01:44 PM.