"If your working on a combination motor starter that has the exposed disco open is it considered live work?"

Depends on what you are doing

"IS live testing concentered working live work?"

That is an exception to the EEWP requirement, so no it is not. However you still need to wear the proper PPE.

"Is working on or around cycling equipment considered live work?"

Again, depends on what you are doing. Any interaction with the equipemt requires PPE for arc flash protection even if live parts are not exposed.

"What is considered a high energy circuit?"

Thats a pretty vauge question. The IEEE 1584 addresses arc flash hazards for 208V systems if the suppling transformer is > 125kVA, thats where the arc is self sustaining and relies on a protective device to clear it.

"I guess im trying to find out when PPE becomes necessary.Any links you may have would be greatly appreciated."

You will find PPE necessary for most tasks, typoically the arc flash hazard on 480V systems is greater than that on 13,800V systems. You can find arc flash info at www.epowerplus.com

"Seems everyone has differing opinions."

Who is everyone? Either you are in compliance with the 70E or you are not, be careful who you listen to. Sounds like you need some training on the topic.I notice you are in Windsor, there is a 70E compliance course in the Detroit area every month, next one is June 7th-8th.




MV/HV Testing Specialist, "BKRMAN"