Caper:

That practice was not unusual. I have seen electrical contractors from the East to the West coasts, did do it the way you describe.

It was not covered, until Andy Cartel sent in a proposal for the 87? NEC to make sure the rule required the EGC's to be inside the box.

Here's the current rule in the 2002 NEC:

250.148 Continuity and Attachment of Equipment Grounding Conductors to Boxes.

Where circuit conductors are spliced within a box, or terminated on equipment within or supported by a box, any separate equipment grounding conductors associated with those circuit conductors shall be spliced or joined within the box or to the box with devices suitable for the use.


Joe Tedesco, NEC Consultant