INTERNATIONAL COLOR CODES FOR CONDUCTORS PER SYSTEM TYPE AND VOLTAGE

Please note: This list has been compiled from multiple sources and is BELIEVED TO BE CORRECT, but the data HAS NOT BEEN VERIFIED for accuracy per currently used International Color Schemes.

The Members here at ECN have supplied a majority of the information, and I would like to thank them personally for their contributions!!!

If you have questions, comments, or would like to submit additional data to this list, feel free to contact us at ECN.
Either contact me via E-Mail or a posting at the General Discussion area, or contact one of the other Moderators. Alternately, contact the site Webmaster.

Scott Thompson. (Scott35)


Color Codes: United States.

Note: The following Color Codes are in Five (5) separate sections.

-------------------------------------------
-------------------------------------------

Section #1: NEC® Specified Color Codes for Conductors:

BASICS:

* GROUNDED SYSTEM CONDUCTOR (Identified Conductor): White, Gray
(includes "Neutrals" or "Commons", along with any other Grounded Conductor.);

* EQUIPMENT GROUNDING CONDUCTOR: Green, Green w/ Yellow Stripes, Bare;

* UNGROUNDED CONDUCTOR(s):


--60 VAC to 600 VAC--
  • Black, Red, Blue, Brown, Orange, Yellow, Pink, Purple (Violet).


--120/240 V 3Ø 4 Wire Delta "High Leg"--
  • Orange.


2002 NEC® Index - Color Codes:

* Branch Circuits: 210.4(D), 210.5;

* Conductors: 310.12, 504.80(C), 647.4(C);

* Grounded Conductor: 200.6;

* Grounding Conductor: 250.119, 310.12(B), 400.23;

* Heating cables: 424.35;

* Feeders: 215.8;

* Panelboards: 408.3(E);

* Sensitive electronic equipment: 647.4(C);

* Service-entrance conductors: 230.56.

Note: Green with yellow stripe(s) is often used for the Equipment Grounding Conductor (EGC) that is isolated. The use of a Conductor with 3 continuous White Strips along the entire length, is acceptable for identification of the Grounded Circuit Conductor.

(Thanks To Joe Tedesco for the 2002 NEC® references!)

---------------------------------------------
---------------------------------------------


Section #2: Trade/In-Field Preferred Specific Color Codes for Conductors:

........................................

60/120 VAC 1 Phase 2 Wire System (Isolated SDS System):
  • Ungrounded Conductors: Black/Red, or Black/Blue;
  • Equipment Grounding Conductor: Green.
  • Note: This system does not have a Grounded Circuit Conductor.


.............................................

120 VAC 1 Phase 2 Wire:
  • Ungrounded Conductor: Black;
  • Grounded Conductor: White;
  • Equipment Grounding Conductor: Green.
  • Note: If part of a Multiwire circuit, or from a Multiwire system, Ungrounded Conductor takes the "Line" color.


.............................................

120 / 240 VAC 1 Phase 3 Wire:
  • Ungrounded Conductor: Line 1 ("A") = Black;
  • Ungrounded Conductor: Line 2 ("B") = Red;
  • Grounded Conductor: White;
  • Equipment Grounding Conductor: Green.


.............................................

208Y/120 VAC 3 Phase 4 Wire Wye System:
  • Ungrounded Conductor: Phase A = Black;
  • Ungrounded Conductor: Phase B = Red;
  • Ungrounded Conductor: Phase C = Blue;
  • Grounded Conductor: White;
  • Equipment Grounding Conductor: Green.


.............................................

120/240 VAC 3 Phase 4 Wire Delta System:

- At Main Service:
  • Phase A = Black;
  • Phase B = Blue;
  • Phase C = Orange (High Phase To Ground);
  • Grounded Conductor: White;
  • Equipment Grounding Conductor: Green.


- Other Panels:
(i.e.: Subpanels, other than main panels):
  • Phase A = Black;
  • Phase B = Orange (High Phase To Ground);
  • Phase C = Blue;
  • Grounded Conductor: White;
  • Equipment Grounding Conductor: Green.


.............................................

480Y/277 VAC 3 Phase 4 Wire Wye System:

*** ---Option 1--- ***
  • Phase A = Brown;
  • Phase B = Orange;
  • Phase C = Yellow;
  • Grounded Conductor: Gray (or White);
  • Equipment Grounding Conductor: Green.


*** ---Option 2--- ***
  • Phase A = Brown;
  • Phase B = Purple / Violet;
  • Phase C = Yellow;
  • Grounded Conductor: Gray (or White);
  • Equipment Grounding Conductor: Green.


.............................................

240, 480 or 600 VAC 3 Phase 3 Wire "Corner" Grounded Delta (w/Phase "C" Grounded):
  • Ungrounded Conductor: Phase A = Black;
  • Ungrounded Conductor: Phase B = Red (or Blue);
  • Grounded Conductor (Phase C): White;
  • Equipment Grounding Conductor: Green.


.............................................

240, 480 or 600 VAC 3 Phase 3 Wire Ungrounded Delta:
  • Circuit Conductor - Phase A: Black;
  • Circuit Conductor - Phase B: Red;
  • Circuit Conductor - Phase C: Blue;
  • Equipment Grounding Conductor: Green.


.............................................

Grounding Electrode Conductor color:
  • Black.


.............................................

Isolated Grounding Conductors ("IG"):
  • Green w/ Yellow Stripes.


---------------------------------------------
---------------------------------------------

Section #3: Grounded Conductors between Separately Derived Systems (AKA "SDS"):

* Grounded Conductors on System with the HIGHER Voltage (System which normally feeds the Transformer):
  • Gray.


* Grounded Conductor On the SDS Secondary (output) side:
  • White;
    or
  • White w/ black stripes.


---------------------------------------------
---------------------------------------------

Section #4: Flexible Cords:

2 Wire Cords:

* Ungrounded Conductor: Black;
* Grounded Conductor: White

.............................................

3 Wire Cords:

* Ungrounded Conductor: Black;
* Grounded Conductor: White;
* Equipment Grounding Conductor: Green.

.............................................

4 Wire Cords:

* Ungrounded Conductors: Black, Red;
* Grounded Conductor: White;
* Equipment Grounding Conductor: Green.

.............................................

5 Wire Cords:

* Ungrounded Conductors: Black, Red, Blue;
* Grounded Conductor: White;
* Equipment Grounding Conductor: Green.

---------------------------------------------
---------------------------------------------

Section #5: AC / MC and NMC Cable Conductor Color Codes:

2 Wire Cable:

* Ungrounded Conductor: Black;
* Grounded Conductor: White;
* Equipment Grounding Conductor: Green.

.............................................

2 Wire Cable - w/ IG:

* Ungrounded Conductor: Black;
* Grounded Conductor: White;
* Equipment Grounding Conductor: Green;
* Isolated Grounding Conductor: Green w/ Yellow Stripes.

.............................................

3 Wire Cable:

* Ungrounded Conductors: Black, Red;
* Grounded Conductor: White;
* Equipment Grounding Conductor: Green.

.............................................

3 Wire Cable - w/ IG:

* Ungrounded Conductors: Black, Red;
* Grounded Conductor: White;
* Equipment Grounding Conductor: Green;
* Isolated Grounding Conductor: Green w/ Yellow Stripes.

.............................................

4 Wire Cable:

* Ungrounded Conductors: Black, Red, Blue;
* Grounded Conductor: White;
* Equipment Grounding Conductor: Green.

.............................................

4 Wire Cable - w/ IG:

* Ungrounded Conductors: Black, Red, Blue;
* Grounded Conductor: White;
* Equipment Grounding Conductor: Green;
* Isolated Grounding Conductor: Green w/ Yellow Stripes.

Note: This list of Cables describes the colors found in many commonly used AC / MC and NMC Cables. There are many other color schemes available. Refer to Manufacturers' listings for further information.

--- end of United States information ---
(text edited 01.13.2006 by S.E.T., to include listing bullets and typeset changes)
---------------------------------------------
---------------------------------------------


Current British standards

Current British standard, fixed cables (A,B,C,N,Gnd):

Red, yellow, blue, black, green/yellow
(Plain green for ground until 1980s.)

Pre-1965 installations:
Red, white, blue, black, green

Flexible cords, current standard:
Brown (all phases), blue, green/yellow

Pre-1970 cords:
1-phase: Red, black, green
3-phase: Red, white, blue, black, green

The green/yellow earth wire has been recognized since the 1960s, although only for the EGC in a cord.

The 1966 IEE Regs. specify only plain green, but the green/yellow was added as an amendment sometime later. The 1970 revised edition specifies green/yellow as being the only acceptable colors for a cord EGC, along with brown & blue in place of the old red & black for line & neutral respectively.

A few appliance cords made probably during late 1969/early-1970 period which actually have red & black along with a green/yellow ground. I'm not sure if these were British-made, or possibly Continental done for the U.K. market.

Thanks to Paul ("PaulUK") for the above information!


Bahamas:

Black,Red,Blue,white 120/208
Brown,Orange,Yellow,white 277/480


Sweden:

Prior to 2002:

(L, N, PE)
Black, Blue, Green/Yellow

(L1, L2, L3)
Black, Brown, White or Black or Black/White or (wires in conduit)
Orange or Grey

Prior to 1973


(L, N, PE)
Black, White, Red

3-phase and light switches
Black, Blue and/or Yellow and/or Grey and/or Green.

Colour of the protective earth conductor.
(For Sweden)

Prior to 1960: No rules
1960: Red for cables; red or g/y for flexes
1968: g/y for both cables and flexes (transition period until 1972)



Denmark:


I think the old (prior to 1973) code was:
(L, N, PE)
White, Black, Red

3-phase or light switch
White, Brown and/or Grey and/or Blue and/or Yellow and/or Green
(Order unknown)

Mains Cords; Europe:
By this we mean flexible appliance wiring or line cords, not the fixed
cable or wiring inside the walls. All colour code combinations are
given in the order L, N, E: In other words line (live), neutral and
earth (ground).

The current general standard is Brown, Blue, Yellow/Green striped
and this is mandatory in most European countries and on items
intended for sale in those countries. The colours were chosen not
for their association (otherwise brown would be earth!) for reasons
set up below.

Elsewhere in the world and also in Europe in previous times, these
colour codings vary widely. The following combinations can be
encountered. Again the order is L, N, E and the list is not intended
to be exhaustive.

Belgium: Red, yellow or blue, Grey, Black.
Germany: (L, N, Gnd): Black, Gray, Red.
Great Britain: Red, Black, Green.
Netherlands: Any colour but Gray or Red.
Russia: Red, Grey, Black.
Switzerland: Red, Grey, Yellow or yellow/red.

The foregoing should make it clear why a unified colour coding of
wires was necessary. Green is by no means the obvious colour for
earth either:
before standard colours were adopted, earth was red in Austria,
Finland, Germany, Norway, and Sweden; black in Belgium and Russia,
Gray in the Netherlands and Poland, yellow in Switzerland and green
in Britain and North America. Three cheers for standardization!

The choice of colours for the world-wide system was not arbitrary
either; earth (ground) had to be distinguished and making it striped
was an inspired choice. The other two colours had to be clearly
distinguishable, even by people who suffer colour-blindness, and
blue and brown were judged the most clearly different shades by experts in this field.

France:
(Old System)

Phase 1: Green (Vert),
Phase 2: Yellow (Jaune),
Phase 3: Brown (Marron),
Neutral: Grey (Gris),
Earth: White (Blanc)

According to a reference, the old French color code used up until 1970 and was:

Phase = Green
Neutral = Red
Earth = White or Gray

Current French Standard:

Phase A: Black (Noir),
Phase B: Red (Rouge),
Phase C: Brown (Marron),
Neurtal: Blue (Bleu),
Ground: Green / Yellow (Vert/Jaune)

Please refer to discussion thread in Non-US Electrical Systems titled:
International Wire Colour Codes
and refer to posts by Moderator and Members referring to discussions in French Newsgroups regarding the color codes.

Old German / Austrian Color Coding:

flexes:
P: black
N: grey (can be connected to ground terminal of receptacle with
jumper to neutral, TN-C)
G: red
L2, L3: black, blue
fixed wiring: single phase: see flexes
2 switches in one box: feeder black, switch loops grey and red
3 ph: 4w
R,S,T: black, blue, red, neutral (usually only ground) grey, red one
can be pink as well, was also commonly used for flexes, this was the
most common wiring arrangement.
5w (pretty rare): see flexes.
As you see this system was rather inconsequent, and this is one
reason why it was phased out.
However, 4w 3ph systems still have black, brown, blue for phases
and y/g for ground.

Anyway, this color code is definitely NOT reliable, even electricians
usually took whatever wire color was just handy!

Current Austrian Color Code:

(L1, L2, L3, N, GND): Black/Brown/Grey/Yellow-Green.

Until 01/01/02 (probably) L2 and L3 both black.

Old work (pre 1970) Black, blue, pink, grey and red (no idea about phase order)


----------end as of 12.28.2002-------------

Feel free to contribute to this list!

Scott s.e.t.
M. post: 12.28.02 20:53:00 PST

Revision #1: 01.05.03
Additional items posted as replies:
#1: 01.05.03

edit refers to revisions.

P.S. once this list becomes completed and correct, I will repost the completed compiled list under a new topic heading within this forum.

Scott.

[This message has been edited by Scott35 (edited 01-05-2003).]

[This message has been edited by Scott35 (edited 01-13-2006).]