Quote
At the bottom of the picture, there is an erratum note, does that refer to the Spur box having two fuses, instead of the usual 1 fuse in the Phase?
Yes. By the time this edition of the Regs. was in force it was certainly not considered acceptable to fuse the neutral.

Quote
As in, you wouldn't be allowed to have a spur coming off every point on the ring would you?
Actually, yes! --- "Not more than half the sockets installed may be served by spurs."

You can see the similar limitation in point #5 of the modern 16th edition here .

What has changed is that the 13th edition allowed a spur to feed two individual socket outlets whereas nowadays a spur may feed only one (although it may be a double socket).