I run #12 NM using 3 wire to run 120V smokes and share with a lighting circuit. The smokes have #18 wires to tie into. I am wondering about this reduced wire size being an issue. I know the things dont use much juice, but it seems odd to tie in #18 to a 15 or 20 Amp circuit. Is this a bad design or do the smokes' wires in the J-box count as part of the internal workings of the fixture?

Is there an article on this issue I can read up on?

Thanks in advance.