Assuming one 20 amp circuit I would use a 3.O KVA 277 to 120 transformer.

This should be a shelf item at a major supply house.

Square D, GE, Jefferson and many others make them.

Than you need to go to 250.30 for grounding this transformer and Article 450 for overcurrent protection of it.


Bob Badger
Construction & Maintenance Electrician
Massachusetts