I have was taking amperage measurements on some PSC motors and found that the common wire would have a higher reading than the run wire. In one or two cases the higher reading was above the full load amps of the motor while the other reading was below the fla. The motors were not heavily loaded. Which reading should be used for the comparison to the fla. Thanks.