Quote
Couldn't understand why I got 120 or 208 no matter where I placed the breaker until I really looked and saw neutral on hot side of the 2 pole switched neutral breaker
.
After opening pumps to make sure it wasn't reversed there, I fixed the mix up yesterday.Kinda odd as the rest of the job was neat and workman like. I'm sure he/she had a brain cramp [Linked Image]

[This message has been edited by walrus (edited 11-16-2004).]