I am a Licensed Journeyman Electrician living in Colorado. I live in a condo and our association hosted a walk through last week to discuss items needing repair. I pointed out the following and our manager dismissed them either as not being a priority or too expensive to repair.
This particular photo shows a lighting repair made in a carport. It would appear the grounds were removed from the romex cables, and the junction box left open.
This photo illustrates schedule 40 PVC used to energize light poles. It would appear the PVC is at a burial depth of only 4 inches.
This photo illustrates the improper use of non-metallic cable, a similar method used throughout the complex, more photos to follow.
This picture shows a disconnect for an air conditioning condenser no longer supported. It is held in place only by the conduit attached.
This photo shows another problem with the air conditioning condensers...adequate protection to ensure cars aren't running into them has not been provided in my opinion.