Any idea what the capacity of the transformer is? Judging from its physical size, it doesn't look to be much larger than required to simply power the two lamps (the original intent, of course). It also appears that the lamps are burned out or have a lot of hours on them.
One more question; is the 277v. entry in the back center of the fixture? If so, it looks kinda like NM cable.
From an old codebook (I have a new one coming); Art. 700-13 - "No appliances and no lamps, other than those specified as required for emergency use, shall be supplied by emergency lighting circuits."
[This message has been edited by mamills (edited 08-14-2002).]