Quote
[Linked Image]

The first photo is of the "new" panel, a 6 circuit, 3R, MLO. Not nearly enough room for the mobile home, let alone the addition to said mobile home and the circuits required. It was replaced with a 22 space 100 A with Main CB

[Linked Image]


The second pic is a close-up showing the conductor shorted to the meter base frame

[Linked Image]

The third photo shows the cut neutral strands so the conductor would fit into the 100 Meter base that was here before the inspection and was "repaired" with a 200A before I came along.

[Linked Image]

Photo #4 shows the modified dead front for the 3R 200A Panel, very sharp and jagged too.

[Linked Image]

Photo #5 is another shot of the meterbase "before"...

[Linked Image]

The 6th photo is the after pic of the meterbase, just for comparison.

Not shown, open splices, cut cables, loose acorns on the ground rods, no back-fill on the conduit (and too shallow), no treated lumber, and snakes and bugs galore....

All this and a little yippy, biting dog...

-Virgil