Photo's and information submitted by RODALCO:
Quote
These first two pics were from a streetlight pole in Kelston which supplies a bus-stop also, it was not working so I had to pull all these wires out of the pole to do some checks. Earth wire was not connected as you can see the cut lug which was supposed to sit under a loose stud in the pole. Final result was wiring ok. just a blown fuse in lighting armature bus-stop. good checking from whoever looks after those bus-shelters.
they blamed a cable fault in the TPS.

[Linked Image]


[Linked Image]

Quote
The next 3 pics are from HW (hot water) pilot fuses on a piece of cardboard in a transformer in Beach Haven. After an HT fault I had to backfeed the LT side, remove the jumpers from the LT bushings to get the power back on.
Probably about 20 years ago, whoever did the job made an attempt to affix the fuses. The card board is just about to fall apart.
Very often pilot fuses are just laying on the bottom of the TX.

The jumpers are visible at the bottom, green 70 mm² earth wire with coloured tape on it.


[Linked Image]


[Linked Image]


[Linked Image]

Thanks a heap Ray!. [Linked Image]