The problem I see is the disconnect is a tap of a tap.

It looks like a fat 10 awg or skinny 8 awg was already a tap feeding a disconnect so this second tap could overload the first tap.

Is this the service for a building?

How many disconnects are here, more than 6?

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts