Rule 12-120(2)

Conductors in vertical raceways shall be supported independently of the terminal connections and at intervals not exceeding those specified in Table 21 and such supports shall maintain the continuity of the raceway system without injury to the conductors or their covering.

Intent for Rule 12-120(2).

We intend that the weight of conductors, when mounted in the vertical position, not be supported at electrical equipment terminations. When the weight is considerable, the top support alone should not be relied on; intermediate supports should also be used. Conductors installed in vertical raceways are to be supported in accordance with Table 21.

Field Considerations for Rule 12-120(2).

There are types of single- or multi-conductor cables that because of their construction have, when run vertically, similar problems as conductors installed in vertical raceways. The cable manufacturer should be consulted to determine the maximum vertical run between conductor supports, or cables specifically designed to be run vertically should be used.


Tie wraps are intended and approved for securing cables and conductors in place for spacing, but not for supporting them.

This means tie wraps may not bear any weight.

Tie wraps are not permitted to support cables in vertical sections of cable tray.
Tie wraps may be used in horizontal sections of cable tray to maintain cable spacing.

Tie wraps shall be suitable for the environment (indoor, outdoor, sunlight, etc)

Tony Moscioni
Electrical Inspector
Electrical Safety Authority