ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 104 guests, and 12 robots.
Key: Admin, Global Mod, Mod
Previous Gallery
Next Gallery
Print Thread
Rating: 5
Page 2 of 2 1 2
#181951 11/11/08 10:57 PM
2 Images
Joined: Dec 2000
Posts: 4,294
Member
Double Lugging

#12 on a 60 Amp circuit
and
#12 on a 30 Amp circuit
Last edited by electure; 11/15/08 04:39 PM. Reason: add images
14 Comments
HotLine1 #211067 09/10/13 01:02 PM
Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
Originally Posted by HotLine1
One comment I heard a while back was something like.....

"I'm using the <10 foot tap rule! The small motor only draws 7 amps, so the 60 amp is still not overloaded"



I bet you got a chuckle out of that.


Greg Fretwell
electure #211068 09/10/13 02:57 PM
Joined: Dec 2000
Posts: 4,294
Member
Greg, I stand corrected.

Another product, maybe a lighting contactor, that I'd come across was listed for 2 conductors per terminal, with the same #14-#8 range.
It had a different torque value given for #8-10 than the #12-14

I got a 30A QO this morning with 30ft pounds given for the torque, no matter what the use (although it says that AL wire may not be used for the 2 wires per terminal application).

electure #211073 09/11/13 01:56 AM
Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
I think the different wire size thing on a QO is somewhat limited by use. The wobble plate terminal only goes on breakers up to 30a (hence the 8ga for AL) and you usually are going to be using the appropriate wire for the breaker.

If I saw radical differences in wire side the whole thing would get a second look to see what was going on here.


Greg Fretwell
electure #211122 09/16/13 11:59 PM
Joined: Dec 2000
Posts: 4,294
Member

The double lugging problem was probably the least of their worries.

These were taken at the same place.


https://www.electrical-contractor.net/forum/el/sw4801.jpg


https://www.electrical-contractor.net/forum/el/sw4802.jpg

as a result of using 2 pole 277V single circuit switches with 480V between the poles.

The contractor that did it had the company motto:
"Leaders of Innovation" rolleyes

electure #211166 09/22/13 08:32 PM
Joined: Sep 2013
Posts: 43
Member
There's nothing legal with what I'm looking at .. The main problem is the micro arcing that goes on especially if two different wire sizes are sharing a common connection plate .. that would be my take .. besides the lower amperage wires tapped into the heavier breaker is an obvious issue ..


Anyone claiming to know everything about Electrical, is wrong.